Storm Inspection Report
TABLE OF CONTENTS
I. Introduction
II. Background & History
III. Wind Loads
IV. Wall Diaphragms
V. Repairs
VI. Summary
I. Introduction
The site was inspected by Tom Price, a
licensed professional engineer. The
inspection
lasted approximately 1/2 hour. Also
present were representatives of the
insurance
company.
II. Background & History
The home is a one storey wood framed
structure on a crawl space, with a main
gable ridge
axis running approximately north-south.
two hip roofed extensions extend to the
east and
to the west. It is built with materials,
structural systems, and utilities very
common
for this type of home.
A storm on the night of 5-18-97 created
wind load conditions severe enough to
cause sig-
nificant damage to the property. The
extension to the west had its roof lifted
off in the
storm, causing structural damage to the
entire extension.
III. Wind loads
Wind loads create lateral and uplift
forces on structures. A wood framed
structure of this
type achieves its lateral load resisting
capability primarily from diaphragm
action of the
roof, wall, and floor sheathing, and
diagonal bracing if present. The loads
induced on the
house have caused distortion of various
diaphragm surfaces. Only careful
measuring with
appropriate measuring tools can tell just
how out of plumb, level and square the
house
currently is.
IV. Wall diaphragms
There are numerous locations where the
wall to ceiling rdywall joint has failed
longitud-
inally. This is due to large lateral
forces occurring in the plane of the
wall. In walls
that show visible distress to the rdywall
itself, the taped joints, and/or the
fasteners,
it must be assumed that the rdywall is no
longer acting as a rigid diaphragm, and
must be
replaced. It also is likely that the wall
has been racked out of its original
position.
This causes doorways to change shape,
making the door difficult or impossible
to close.
V. Repairs
All walls and ceilings should be checked
for damage to rdywall. Any distress of
fasteners
and taped joints, or loosening of rdywall
boards from the studs/ceiling framers is
cause to
remove wall boards, true up all framing,
and replace wall boards. Framing members
should
be thoroughly checked for damage.
Even if framing members are deemed to be
in usable condition, all wall, floor, and
roof
areas must be brought back into a plumb
and square condition prior to
installation of new
sheathing materials. Proper measuring
devices such as transits, levels, steel
measuring
tapes, and others must be utilized to
determine plumb, level, and squareness of
the various
diaphragm surfaces of the house.
Where framing members have clearly been
damaged, such as west extension,
replacement of
materials is necessary. The west
extension area likely needs to be
completely re-framed,
though re-use of undamaged framing
members and undamaged exterior sheathing
is acceptable.
The anchorage of the west extension to
the foundation must be checked and
repaired to code
requirements. Proper bearing and
anchorage to foundation must be assured.
Any existing materials re-used In the
reconstruction must be inspected
carefully for damage.
If there is any doubt about a structural
member, it should be replaced.
Any wall, floor, or roof assemblages
being considered for re-use must be
thoroughly
inspected and brought into tolerance for
plumb, level, and squareness.
Vl. Summary:
- The west extension of the house
received significant damage, and will
likely require a
complete rebuild. Re-use of undamaged
framing members and exterior sheathing
may be
considered.
- The entire home needs to have all
walls, floors, and ceilings checked for
plumb, level
and squareness, as well as distress to
sheathing and fasteners. Damaged areas
should have
sheathing removed, framing members trued
up and checked for damage, and sheathing
replaced.

Contact
Information
- Telephone:
- (517)
467-6145
- FAX:
- (517)
467-2220
-
- Postal
arddess:
-
- Structural
Solutions LLC
- 8466 Slee
Rd.
- Onsted, MI
49265
- Electronic
mail:
General Information:
Thomas R. Price,
P.E.

[ Home ] [ Engineering Services ] [ Gallery of Projects ] [ Request For Quote ] [ Resources ]
Copyright ©
2007 Structural Solutions LLC, 8466 Slee Rd.
Onsted, MI 49265 Lenawee County
|