- Sample of a code
review
CODE REVIEW
Code review for structural loading
requirements:
Project: 110' x 3272' building
65' x 120' building
Code: 1998 State Building Code 675 IAC
13-2.3
Building Occupancy:
312.1 States that Class 1 agricultural
buildings are to be classified as Group
U-1.
A class 1 structure is one which is
entered by one or more employees, or is
open
to the public.
312.2.2 States that would-be U-1
buildings exceeding 1000 sq. ft. shall be
classified
as one of the other occupancies most
nearly resembling its use. Occupancy F-2
is the
likely the best fit. F-2 allows unlimited
area if a 60' clear yard exists all
around the
building. (505.2) Under F-2, the 20 psf
snow load called for in Table 16 would be
required.
312.6 In cases where this type and size
building is deemed by the local authority
to
not be class 1, the project need not be
submitted to State Plan Review. The local
authority is free to regulate the
project. In these cases the local
authority should be
consulted for loading requirements.
Per County Buildings Dept, this project
would be considered Class 1, and
submittal to State Plan Review is
required. See p. 2 summary of design
criteria.
Design criteria summary for Class 1
Agricultural , >1000 ft^2:
Code: 1998 Building Code
Occupancy: F-2
Type of Construction: II-N
Dead load: Per building manufacturer
Snow load: 20 psf (Table 16)
Live load: 16 psf purlins (for 4:12 min.
roof slopes)
12 psf frames
Wind load: 75 mph (Exposure to be
determined according to site)
Seismic: zone 1

Contact
Information
- Telephone:
- (517)
467-6145
- FAX:
- (517)
467-6145
-
- Postal
arddess:
-
- Structural
Solutions LLC
- 8466 Slee
Rd.
- Onsted, MI
49265
- Electronic
mail:
General Information:
Thomas R. Price,
P.E.

[ Home ] [ Engineering Services ] [ Gallery of Projects ] [ Request For Quote ] [ Resources ]
Copyright ©
2009 Structural Solutions LLC, 8466 Slee Rd.
Onsted, MI 49265 Lenawee County
|