report of a structural investigation -
insurance claim inspection report
Customer Name: Insurance Company
Project Name: Residential Home Storm
Damage
Project Location: USA
TABLE OF CONTENTS
I. Introduction
II. Background & History
III. Wind Loads
IV. Wall Diaphragms
V. Repairs
VI. Summary
I. Introduction
The site was inspected by Thomas R. Price
P.E., of Structural Solutions LLC, a
licensed professional engineer. The
inspection lasted approximately 1 hour.
Also present were representatives of the
insurance company, and the owner.
II. Background & History
The home is a two storey wood framed
structure on a basement, basically
rectangular in plan,
with a main gable ridge axis running
approximately east-west. It is built with
materials,
structural systems, and utilities very
common for this type of home. A steel
open-framed
tower of approximately 70 height
stood approximately 10 to 20 ft. from the
house, to the
west.
A recent storm created wind load
conditions severe enough to cause
significant damage to the property. At
least part of the damage to the house was
caused by the tower falling over onto its
west gable end, hitting near the gable
peak.
III. Wind loads
Wind loads create lateral and uplift
forces on structures. A wood framed
structure of this
type achieves its lateral load resisting
capability primarily from diaphragm
action of the
roof, wall, and floor sheathing, and
diagonal bracing if present. The loads
induced on the
house have caused distortion of various
diaphragm surfaces, as well as severe
structural
damage to the north wall of the great
room. Only careful measuring with
appropriate
measuring tools can tell just how out of
plumb, level and square the house
currently is.
It is difficult to assess the exterior
walls as they are covered by siding
outside and rdywall inside,
leaving no way to determine what
diaphragm / bracing materials are
present, and what fastener
quantity and spacings exist. The
condition of the second floor as a
structural diaphragm is not
known since the decking and fasteners are
covered with carpet. Similar uncertainty
exists with
the roof.
IV. Wall diaphragms
There are numerous locations where the
wall to ceiling rdywall joint has failed
longitud-
inally. This is due to large lateral
forces occurring in the plane of the
wall. In walls that
show visible distress to the rdywall
itself, the taped joints, and/or the
fasteners, it must
be assumed that the rdywall is no longer
acting as a rigid diaphragm, and must be
replaced.
It also is likely that the wall has been
racked out of its original position. This
causes doorways
to change shape, making the door
difficult or impossible to close.
V. Repairs
Wall, floor, and roof surfaces that have
been distorted out of original position
must have
their sheathing replaced. The damaged
sheathing, fasteners, taped joints, etc.
cannot be
re-used as load resisting members. The
framing members themselves - studs,
joists, rafters,
etc. may very well be in usable condition
if the distortion of the diaphragm was
small. If
inspection after removal of the sheathing
reveals that the framing members are in
good
condition, re-use of them may be
considered.
Even if framing members are deemed to be
in usable condition, all wall, floor, and
roof areas
must be brought back into a plumb and
square condition prior to installation of
new sheathing
materials. Proper measuring devices such
as transits, levels, steel measuring
tapes, and others
must be utilized to determine plumb,
level, and squareness of the various
diaphragm surfaces of
the house. It is questionable as to
whether it is practical to attempt to
re-square the structure
without dismantling it down to the first
floor. Jacking or pounding one wall back
square and
plumb may cause others to go out of
shape, and it could become impossible to
get everything
square and plumb at the same time. Also,
the jacking and pounding will take its
toll on the
framing materials. If this type of repair
is attempted, it is likely that all
sheathing will need
to be removed from the walls, and quite
possibly the second floor and roof as
well. A qualified
home building contractor should be
consulted for determining the feasibility
of these types
of salvage operations.
Essentially, it may not be cost-effective
to try to reverse what nature has done.
Where framing members have clearly been
damaged, such as the north exterior wall
of the great
room, and the west end of the main gable,
replacement is necessary.
Inspection of the basement and first
floor revealed no significant damage
other than damage
to the floor decking where it appears
that falling masonry from the fireplace
punctured it.
Replacement of affected floor deck is
necessary. It appears likely that the
basement and
first floor framing and decking are in
good usable condition, if it can be
verified that all
surfaces are plumb, level, and square,
and the punctured decking replaced. Floor
anchorage
to the concrete basement wall must be
checked, and reinforced if deemed
necessary.
Any existing materials re-used In the
reconstruction must be inspected
carefully for damage.
If there is any doubt about a structural
member, it should be replaced.
Any wall, floor, or roof assemblages
being considered for re-use must be
thoroughly inspected
and brought into tolerance for plumb,
level, and squareness.
If the 70 ft. tower is to be reinstalled,
it must be inspected for damage to its
structural elements.
It is advisable that the soil bearing
capacity be investigated at the tower
base, and a foundation
base be designed to accommodate the soil
conditions, and the loading provisions
prescribed
by the Building Code.
Vl. Summary:
- Proper measuring devices must be used
to determine how far out of plumb, level
and square
the structure currently is.
- Diaphragm materials that show signs of
distress must be replaced.
- Many individual framing members
throughout the house may be in good
condition.
- Salvaging the structural materials
above the first floor may prove to be too
difficult and costly,
primarily due to the difficulty of
returning structural elements to plumb,
level, and square
condition. There will be many judgment
calls to be made by appropriate
professionals.
The feasibility of superstructure salvage
should be discussed with a qualified
contractor.
- Upon verifying plumb, level, and
squareness, the basement and first floor
stand a good
chance of being re-used without problem.
Anchorage to concrete must be checked.
- If the Steel tower is to be re-erected,
it must be deemed structurally sound, and
a soil capacity
and foundation investigation be made.

Contact
Information
- Telephone:
- (517)
467-6145
- FAX:
- (517)
467-2220
-
- Postal
arddess:
-
- Structural
Solutions LLC
- 8466 Slee
Rd.
- Onsted, MI
49265
- Electronic
mail:
General Information:
Thomas R. Price,
P.E.

[ Home ] [ Engineering Services ] [ Gallery of Projects ] [ Request For Quote ] [ Resources ]
Copyright ©
2007 Structural Solutions LLC, 8466 Slee Rd.
Onsted, MI 49265 Lenawee County
|