Investigation of Existing Columns for New
Mezzanine Loads
TABLE OF CONTENTS
I. Introduction
II. Background
III. Mezzanine Information
IV. Existing Column Checks & Results
V. Proposed Column Modifications &
Solutions
VI. Conclusions and notes
VII. Appendix
I. Introduction
A preliminary engineering investigation
has been undertaken to address the
proposed building changes only as they
affect existing
building columns due to the addition of a
50' x 165' x 12' high mezzanine to an
existing
metal building.
The objective of this engineering
investigation was basically twofold in
nature:
1) to determine the extent of the
structural impact and effects on certain
metal building
rigid frame sidewall built-up columns,
interior pipe columns, along with
specific
endwall columns along line 1.
2) to suggest structural modifications,
changes, alterations or similar
improvements to
the existing columns so that it can
properly support the added mezzanine
loads and
forces.
II. Background
The building in question is a
pre-engineered metal building
manufactured by an MBMA certified
producer. It is
a gabled structure measuring 200' wide by
250' long having a low eave height of 25'
and a
roof slope of 1/4:12.
The primary frames are modular, gabled
rigid frames with spans of 4 @ 50' and
are spaced
at 50' on center with intermediate
sidewall wind columns @ 25' spacings. The
interior
frame columns are 10'' diameter pinned
top and bottom pipe columns. Endwall line
1 is a
post & beam type consisting of 12''
deep built-up and wideflange column
members.
III. Mezzanine Information
Mezzanine size: 60' wide X 165' long X
12' high.
Mezzanine Loads: Total Dead Load = 50 psf
Total Live Load = 50 psf
Total Load = 100 psf
See attached sketches showing the
proposed layout of support steel which
denote 6
different existing column types affected
by the new mezzanine loads.
These columns are summarized as follows:
Designation Type Depth Materials Fy(ksi)
A - sidewall SBU 12" @base Flange:
6" x 1/4" 50
Web: 3/16"
B - interior pipe 10 3/4" dia. X
.365" thick. 42
E - sidewall TBU 21''@base Flange: 10''x
1/2" 50
Web: 3/16"
F - Endwall WF W12X14 wideflange 36
G - Endwall SBU 12''@base Flange: 5"
x 1/4" 50
Web: 3/16"
H - Endwall SBU 12''@base Flange: 8"
x 1/4" 50
Web: 3/16"
All above columns to be field verified.
TBU - Tapered Built Up column
SBU - Straight Built Up column
IV. Existing Column Checks & Results
Column types noted as follows will NOT
receive mezzanine loads:
A, B & E
Mezzanine beams and forces at these
locations to be supported by the
following independent
columns:
4"x4"x3/16" Tube columns;
Fy = 46 ksi
9" x 5" x 3/4" baseplate,
K = 1.0 , pinned top and bottom
2 - 3/4" dia. anchor bolts. Length =
11'-0 maximum
The maximum mezzanine floor area assumed
to be supported by these columns is 325
square feet.
The following is a summary of the results
of the analysis of endwall columns along
line 1
including the new mezzanine forces:
Designation Max .Combined Stress Ratio
Percent Overstressed
Column F 1.03 3.0
@ corner
Column H1 0.647 ---
8 feet from sidewall
Column H2 0.985 ---
34 feet from sidewall
Column G 2.578 157.8
The results indicate that the new
mezzanine loading causes a significant
overstress only
in column type G.
The following section will propose a
reinforcement solution for the
overstressed column G.
V. Proposed Column Modification Solutions
There are three main options which appear
appropriate for the new forces and
conditions:
Option1: Build up and reinforce the
column member by coverplating
to improve its section properties
including moments of inertia, rx , ry,
section modulus,
etc., along with the compression flange
area to accommodate the significantly
increased
axial loads.
Option 2: Replace the existing column
with a new column.
Option 3: Support the new mezzanine loads
with independent, separate columns as is
the
case in the other area of the mezzanine.
Option 1: Column G Coverplating
In order to meet required combined
allowable stresses the existing column
will need the
following field-installed materials:
two --- 2 x 1/2 inch 50 ksi plates field
welded to the girt side inner flange of
the column.
one --- 4 x 1/2 inch 50 ksi plates field
welded to the inside flange of the
column.
Option 3: Replace the existing Column
This option represents a significant
contrast to Option 1 and is not
considered in this
investigation.
Option 3: Add new Support Column
This option represents a significant
contrast to Option 1 and is not
considered in this
investigation.
VI. Conclusions and notes
Only one endwall column (G) was found to
be overstressed and requiring
reinforcement through coverplating.
Assumptions and design consideration for
this
investigation is as follows:
--- The mezzanine system is independently
laterally braced. Columns investigated do
not
carry lateral mezzanine loads or forces.
--- Columns must be properly braced at
the mezzanine level by the mezzanine
system.
--- All built up columns supporting
mezzanine beams must have their
web-flange welds
reinforced on the opposite side of all
conrac welds 6''above and below the
mezzanine
beams.
--- Minimum of 4 rows of two 3/4 ''
diameter bolts for mezzanine framing into
the 3/16"
built up column webs for bearing.
--- All columns materials dimensions to
be field verified.

Contact
Information
- Telephone:
- (517)
467-6145
- FAX:
- (517)
467-2220
-
- Postal
address:
-
- Structural
Solutions LLC
- 8466 Slee
Rd.
- Onsted, MI
49265
- Electronic
mail:
General Information:
Thomas R. Price,
P.E.

[ Home ] [ Engineering Services ] [ Gallery of Projects ] [ Request For Quote ] [ Resources ]
Copyright ©
2007 Structural Solutions LLC, 8466 Slee Rd.
Onsted, MI 49265 Lenawee County
|