INSPECTION - Foundation Frost Heave
I. Purpose of
Investigation:
At the request of the Contractor, a site
inspection of recently poured concrete
foundation
walls was made on 6/18/02. Excessive
cracking in two locations has become a
concern.
II. Description of Structure:
The foundation consists of a residential
basement, with an abutting garage
foundation.
8" poured concrete walls bear upon a
strip footing. The basement foundation is
approximately 4 feet below the garage
foundation. The overdig required for the
basement footing removed soil in such a
way that the garage footing had to be
terminated
about 2 feet short of the basement wall.
This 2 foot gap was bridged with 2x8
timber to
support the wall concrete during the
curing process.
III. Observations:
Excessive cracking was observed at the
two locations where the garage and
basement
foundation meet. The crack pattern is
consistent with soil heaving forces
pushing up
at the end of the garage footing. (See
sketch). Recent weather included
temperature
ranges which could have taken the soil
through freeze/thaw cycles. Because the
footings
do not have the typical 42" of frost
protection, they are far more vulnerable
to heaving
forces.
IV. Recommendations:
Option #1:
On each side of the garage, the cracked
sections form a small region of wall
which
presumably can be removed and re-poured.
The exposed jagged surface is good for
bonding to the new concrete. It would be
advisable to dowel into the existing wall
with reinforcing bars. A specific design
for this can be carried out if requested.
Option #2:
Pressurized concrete epoxy can be used to
fill in the cracks, and bond the concrete
back
together. This should be done only by a
contractor with the experience, equipment
and
training needed for this procedure. The
epoxy contractor must determine if their
procedure is suitable for this particular
application. If the epoxy procedure is
chosen,
there will still be the problem of an
uneven bearing surface at the top of the
wall.
Consideration for grinding this surface
level must be made.
For either repair, the exposed conditions
leading to heave still exist. It should
be
considered that the same cracking may
occur, so long as the air temperature is
ranging
above and below freezing, or the clay
soil is swelling due to moisture during
the wet
season. Option #1 has a better chance of
success due to the ability of the
reinforcing
bars to hold the concrete together until
backfill can be carried out, and
permanent frost
protection is in place.

Contact
Information
- Telephone:
- (517)
467-6145
- FAX:
- (517)
467-2220
-
- Postal
arddess:
-
- Structural
Solutions LLC
- 8466 Slee
Rd.
- Onsted, MI
49265
- Electronic
mail:
General Information:
Thomas R. Price,
P.E.

[ Home ] [ Engineering Services ] [ Gallery of Projects ] [ Request For Quote ] [ Resources ]
Copyright ©
2007 Structural Solutions LLC, 8466 Slee Rd.
Onsted, MI 49265 Lenawee County
|