INSPECTION - Aluminum Platform Design
I. Purpose of
Investigation:
At the request of the Client, we have
performed a
structural analysis of the 4'x4' platform
as described in the specification,
furnished
by the Client. The scope of this
preliminary report includes checking the
current
design for 80 psf floor live load, and
the hanrdail for Code prescribed forces
of
50 lb/ft (uniform load) / 200 lb (point
load).
II. Description of Platform:
The platform consists of nominally 4 ft.
square segments, which are to be
connected
end to end, in order to form a continuous
walkway approximately 18" above the
ground surface. Each segment has 4 legs
which bear upon the ground. Hanrdails
are continuous along 2 opposite edges.
Materials are 6061-T6 aluminum structural
shapes and extrusions. Decking (by
others) is to be 2x6 High Density
Polyethylene
(HDPE) by US Plastic Lumber
III. Analysis:
The various structural members were
analyzed for the loads indicated above.
Floor:
The 1" x 1" tubes and the
1.5x1.5 angles running perpendicular to
each other do not
themselves have adequate strength to
resist the 80 psf floor load. The Client
has indicated that they performed a load
test utilizing 2x6 lumber decking over
the
aluminum framing members, and that the
system held the load with no significant
deformation. Calculations for 1.5"
thick lumber deck boards show that they
have
adequate strength and nearly adequate
stiffness, to span the 5 feet without the
help of the tubes and angles. In the
test, it is likely that the sub-framing
acted
essentially as stiffeners. That is, they
helped stiffen the lumber, but the lumber
itself was stiff enough to prevent the
aluminum framing from absorbing excessive
load.
The HDPE decking called for in the
Architectural specification, however, has
only about
1/10th the stiffness of regular lumber.
(Reference - US Plastic Lumber published
structural properties.) Use of the HDPE
will result in nearly all the load being
transferred into the aluminum subframing,
which cannot resist the 80 psf loading.
The 4" siderail extrusion checked
out as adequate for the loading.
Hanrdail:
The members comprising the hanrdail are
adequate for code loadings. The U-bolt
size
and grade was not noted in the pdf
rdawings. The required diameter likely
falls between 1/4" and 3/8",
depending on material grade.
The 2"x2" tube kickers at 45
deg. angle are necessary for adequate
stiffness and strength.
IV. Recommendations:
If the HDPE decking is utilized, some
sort of modification will be necessary to
bolster
the strength of the aluminum subframing.
V. Referenced Documents:
U.S. Plastic Lumber HDPE Technical Data,
2 pgs.
Page 1

Contact
Information
- Telephone:
- (517)
467-6145
- FAX:
- (517)
467-2220
-
- Postal
arddess:
-
- Structural
Solutions LLC
- 8466 Slee
Rd.
- Onsted, MI
49265
- Electronic
mail:
General Information:
Thomas R. Price,
P.E.

[ Home ] [ Engineering Services ] [ Gallery of Projects ] [ Request For Quote ] [ Resources ]
Copyright ©
2007 Structural Solutions LLC, 8466 Slee Rd.
Onsted, MI 49265 Lenawee County
|