- Load Test - Aluminum
BoaDrwalk
I. Purpose of Investigation:
At the request of the client, we have
performed a
structural analysis of the platform as
described in the pdf files, furnished
by the fabricator
The scope of this report includes
checking the current design for 100 psf
floor live load,
and the handrail for Code prescribed
forces of 50 lb/ft (uniform) / 200 lb
(point) loads.
II. Description of Platform:
The platform consists of nominally square
segments, which are to be connected
end to end, in order to form a continuous
walkway approximately 20 above the
ground surface. Each segment has 4 legs
which bear upon the ground. Handrails
are continuous along 2 opposite edges.
Materials are 6061-T6 aluminum structural
shapes and extrusions.
Note that some different joist members
have been considered. The final design
for this
report utilizes aluminum channel sections
for joists going both directions, which
is not yet
reflected in the fabricator pdf files.
The aluminum floor joists are 2.00
channels oriented for weak axis bending,
with tips
of flanges pointed down. Three upper
joists ran perpendicular to the deck
boaDrs, and
two lower joists ran perpendicular to the
upper joists.
The decking is 1-1/8 deep
polypropylene.
The stiffened version has ¾ square
aluminum alloy hollow extrusions embedded
into the polypropylene at an average
6 o.c.
spacing.
The siderail extrusions are as described
by the section drawing A1.
III. Analysis and Design:
The various structural members of the
assembly were analyzed for the loads
indicated
above. The member stresses were then
compared to allowable stresses as
determined
from the appropriate steel (AISC-ASD) or
aluminum (AA ASM 35) design
specification.
Analysis of the joists revealed that the
center upper joist is overstressed 33.9%,
with
a corresponding deflection of
0.774. The other joists, and the
siderails are within
allowable stress limits. The stiffened
decking is within allowable stress limits
for span-
ning the 16 joist spacing.
It was decided to perform a load test to
determine actual center deflection, and
thereby
be able to back figure center joist
stress using the modulus of elasticity of
the material.
A load test was performed under the
direction of Mr. Price, with the client
and helpers participating. From the test
data, load vs. deflection curves were
generated for overall structure response
to gravity load.
80 lb. sacks were laid on the platform in
layers, allowing for the center
deflection to be
measured at load increments of 12 psf.
The maximum load level was 128 psf. Two
separate tests were conducted: One with
stiffened decking, and one with
unstiffened
decking.
We will use the 128 psf data for
comparison to the 0.774 calculated
deflection since
the calculations included for the dead
load being added to the 100 psf live
load.
Unstiffened Deck:
Use of the unstiffened deck resulted in a
deflection of 0.625. Calculations
show that
this reduces the 33.9% overstress to 8.1%
over. This result indicates that the
unstiffened deck is not suitable for
achieving a 100 psf rating.
Stiffened Deck:
Use of the stiffened deck resulted in a
deflection of 0.438. Calculations
show that
this reduces the 33.9% overstress to
24.3% under. This result indicates that
the stiffened deck is suitable for
achieving a 100 psf rating.
The measured deflection of 0.438
represents the combined deflection of the
siderails and the joists. Calculations
show that the siderail deflection
represents approximately
0.137 of this, leaving 0.309
ascribable to the joists. This is
equivalent to L/200.
Floor live load deflection limits in most
building codes call for a maximum of
L/240 which equals 0.250 for the
spans in question. The L/200 is not a
safety problem. However, it should always
be verified with the end owner and local
building official as to whether they are
insisting on the L/240. It is the opinion
of this design office that for most
outdoor boaDrwalk applications, this
oveDreflection is not a concern. Other
uses of
this structural assembly should be
considered on a case by case basis. The
L/240
criteria is intended for longer spans
(20 +), typical of building
framing, and is intended
to (among other things) ensure that
excessive vibration underfoot of longer
spans does not
occur. The short spans and light self
weight of this platform make it unlikely
that
vibration would ever be an issue.
Handrail:
The members comprising the handrail are
adequate for code loadings. The U-bolt
size
and grade was not noted in the shop
drawings. Use of 3/8 dia. Stainless
steel, or an appropriately coated
3/8 dia. A307 steel, are acceptable
U-bolt choices, Ensure that any material
used does not have adverse reaction to
contact with the aluminum alloy
materials.
The 2x2 tube kickers at 45
deg. angle are necessary for adequate
stiffness and strength.
IV. Recommendations:
The platform can be utilized for 100 psf
floor live load applications, provided
that
the stiffened version of the decking is
utilized, and appropriate approval is
obtained
for relaxing the common L/240 deflection
limit to L/200.
The pdf drawings should be updated to
reflect the member sizes and dimensions
of
the test platform. All weld symbols and
fastener sizes must be called out.
Material
specifications should be listed, along
with notes calling out the design loads,
and
soil pressure of the platform legs. These
updates are required in order for the
drawings
to be considered complete enough for
Professional Engineer certification.

Contact
Information
- Telephone:
- (517)
467-6145
- FAX:
- (517)
467-2220
-
- Postal
address:
-
- Structural
Solutions LLC
- 8466 Slee
Rd.
- Onsted, MI
49265
- Electronic
mail:
General Information:
Thomas R. Price,
P.E.

[ Home ] [ Engineering Services ] [ Gallery of Projects ] [ Request For Quote ] [ Resources ]
Copyright ©
2007 Structural Solutions LLC, 8466 Slee Rd.
Onsted, MI 49265 Lenawee County
|