(517) 467-6145 e-mail us
- Sample report of
a structural investigation - Snow drift
surcharge load
BUILDING INVESTIGATION - Check existing
building for additional snow drift
Project Name: Boiler Room Building
Project Location:
Submitted by Thomas R. Price P.E., of
Structural Solutions LLC, a licensed
professional engineer
I. Purpose of Investigation:
Due to adjacent new building
construction, the boiler room structure
must be checked for its ability to
withstand code required roof snow drift
loads. This report summarizes the results
of our structural evaluation.
II. Description of Building:
The building in question is a
pre-engineered metal building system
manufactured by a n AISC MB certified
producer, designed to Metal Building
Manufacturers Association specification.
Dimensions are 40 x 30 x
22 low eave, single slope 1: 12
roof.
III. History:
Pre-engineered metal building system
drawings were not available, however
exposed framing allowed most necessary
measurements to be made in the field.
IV. Referenced Documents:
None
V. Field Observations and Notes:
Field inspection took place between 2 and
4 PM. Note: measurements of web thickness
for many members was not undertaken, as
no means to do so was available.
VI. Investigation Results:
Roof panels: OK
Purlins: OK
Endwall rafters & columns: OK (Lines
1 & 3)
Rigid frame: Reinforcement needed. (Line
2). See p. 7, 8. Note: the web stiffeners
and diagonal stiffeners shown, can be
avoided if it can be verified that the
frame web thicknesses meet or exceed the
minimum thicknesses called out on p. 8.
All other reinforcement shown is still
necessary.
Foundations: Loading increases are shown
on p. 9. Since no foundation information
is available, an evaluation can not be
made at this time. The load increases are
significant enough that soil pressures
may exceed allowables during drift load
conditions. It is advisable to have these
foundation loadings reviewed by the
geotechnical engineer.

Contact
Information
- Telephone:
- (517)
467-6145
- FAX:
- (517)
467-2220
-
- Postal
address:
-
- Structural
Solutions LLC
- 8466 Slee
Rd.
- Onsted, MI
49265
- Electronic
mail:
General
Information: Thomas R. Price,
P.E.

[ Home ] [ Engineering Services ] [ Gallery of Projects ] [ Request For Quote ] [ Resources ]
Copyright ©
2007 Structural Solutions LLC, 8466 Slee Rd.
Onsted, MI 49265 Lenawee County
|