BUILDING INVESTIGATION
Project Name: Pre-engineered metal
building - roof panel damage
investigation.
Project Location:
Submitted to (Attorneys At Law)
Submitted by Thomas R. Price P.E., of
Structural Solutions LLC, a licensed
professional engineer
I. Purpose of Investigation:
At the request of the owners' Legal
advisors, Thomas R. Price P.E., of
Structural Solutions LLC inspected the
Facility in the attempt to determine the
cause of apparent damage to the metal
standing seam roof panels. In addition,
inspection of a base girt anchorage was
requested and carried out.
II. Description of Building:
The building in question is a metal
building manufactured by an AISC MB
certified producer, designed to Metal
Building Manufacturers Association
specification.
The building is comprised of a 120
wide by 75 long gable roof building
connected to
an 80 wide by 156 long single
slope roof building. Roof slopes are
1:12. (ref. Fig. A)
The roof is a 24 wide 24 ga.
galvalume standing seam system. Roof
panel splices exist on 80 roof
areas, with panels approximately 40
long being utilized. Frame spacings are
25. Purlins are cold-formed zees
with 5-6 spacings typical.
III. History:
Building manufacturer drawing dates
indicate that the building is less than
two years old. Some time after the roof
was installed, damage to roof panels was
discovered. This damage exists in two
distinct areas of the roof. (ref. Fig. A
- areas A &
B). A search for the cause of
this damage ensued, including this office
being brought in
to investigate.
IV. Referenced Documents:
Metal building system manufacturer
drawings.
Project drawings, by Project Architect.
V. Field Observations and Notes:
The inspection took place between 1:00 pm
and 3:30 pm. Weather was clear, with a
temperature of approximately 60 °F.
Present on the site was representatives
of the contractor, the owner, and Mr.
Price. Our comments relative to the
inspection of the main building are
listed below.
It must be noted that all details and
materials of construction are not readily
visible and verifiable without some
disassembly of the building system. No
disassembly was done during the
inspection.
Area A:
1) Across approximately 25 roof panels, a
line of damage exists consisting of panel
distortion and localized buckling of the
panel material. The damage is within a
few
inches of each panels midpoint
(20 from end of 40 panels).
The damage location
shifts up and down slope +/- 4:
From the north, the damage location is
consistent
across about 8 panels, then shifts
downslope 4 across 9 panels, then
shifts 4 down-
slope across 1 panel, then upslope
4 across 3 panels, then downslope
4 across
4 panels. Some panels display more damage
than others, but there is a distinct
start and end of the line of damage.
2) The roof panel deformations are
consistent with that caused by excessive
bending at
the damaged location. Specifically,
negative bending (ribs in tension, flat
region in
compression), was the cause of the
damage. The ribs are bowing upwaDr, as
installed, indicating elongation and
therefore tension in the ribs. The
bottom, flat
region of the panels are buckled,
indicating compression in the flat
region.
3) Damage to some of the ribs is such
that the weather tight seal between
adjacent
panels is questionable. Hammer marks on
some of the ribs indicate an attempt
to straighten the rib region, probably to
get the ribs to engage and seal. There is
evidence of water collecting in the
depressions at damage locations.
4) The location of the damage relative to
the panel support points (i.e. the
66 spaced
purlins) is variable, due to the shifting
of the damage location from panel to
panel.
(See Figure B). The damage falls as close
as 2 from midspan, and as far as
9
from midspan. If the damage occurred
after the panels were installed, only an
upwaDr
force on the panels can cause the type of
damage present. Wind uplift is the only
environmental load that could cause this
damage.
If a uniform uplift load is applied to
the panels, the resulting bending force
at the supports (negative bending) is
approximately 3 times the bending force
at
midspan (positive bending). Th building
manufacturer's published panel section
properties indicate that their
24 ga. standing seam roof panel has
nearly equal allowable moments for
positive and negative
bending. This would indicate that
excessive wind uplift will damage the
panels
at the supports first, however, no damage
was apparent at the supports.
If wind uplift were the cause of damage,
the damage locations would not be
suddenly moving up and down slope in
stairstep fashion, as observed.
The amount of buckling that exists would
require large midspan deflections
inconsistent with complete lack of damage
at the supports.
5) The possibility of damage to the
panels occuring prior to installation
must be
reviewed. The damage locations are nearly
centered on the 40 panels.
The metal building manufacturer's
drawings indicate that a spreader beam be
utilized in picking
up bundles of panels which exceed
25 in length. If the panels were
picked
up by a hoist attached just at the center
of the bundle (no spreader beam),
the resulting damage would be quite
consistent with the damage observed:
Ribs go into tension, flat region into
compression, and large deformations
occur. The stairstepping of the damage
location is possibly due to the panels
sliding during the pick, or being stacked
in a manner where the panel ends are
not all lining up in the bundle.
If a bundle of panels were to fail in
this scenario, it is likely that the
panels towaDr
the bottom of the bundle would suffer
more damage than those towaDr the top of
the
bundle. This would explain the
variability of the extent of damage from
panel to
panel.
The metal building manufacturer has
indicated that a maximum of 30 panels are
packed in each bundle.
The observed damage was to 25 consecutive
panels.
Area B:
1) Damage in this area affected 4 panels.
The deformations are similar to area A
However, there are three locations along
the panels exhibitng damage. These
locations, like area A, do not coincide
with the locations of maximum bending,
where damage would occur first under wind
uplift.
2) There is caulk on the side of the
panel rib at two or more damage
locations.
It appears to be covering holes in the
panels, though it was not removed to
confirm this.
Base Girt:
1) An inspection of one segment of the
exterior building wall was unable to find
any anchorage of the base girt to the
foundation.
2) Building manufacturer drawings
indicate 2 -3/8dia. expansion bolts
at 4-0 spacing is required
for base girt anchorage.
VI. Conclusions:
The most likely cause of the roof panel
damage was some sort of mishandling of
the panels prior to installation.
Damage in area A is consistent with what
can be expected when a bundle of panels
is hoisted by picking them up with a
single pick point at mid length of the
panels. It is not consistent with damage
that would occur due to wind or gravity
loads.
Damage in area B is not consistent with
what would be expected from wind or
gravity loads. Some sort of mishandling
prior to installation is more likely.
VII. Recommendations:
It is recommended that the most likely
cause of panel damage be investigated
further; the handling of the panels prior
to installation. This would include
the manufacturer's handling of the panels
in their shop, handling of the panels
during loading onto
truck, shipping, handling of the panels
during unloading at site, and handling of
panels as they were hoisted onto the roof
and installed.
The erector should be consulted as to
when damage was first noticed, when was
caulk applied to ribs and why, whether an
attempt was made to beat the panels
back into shape with a hammer or similar
instrument, whether the panels were
lifted accoDring to manufacturer
guidelines, and whether any incidents
occurred during lifting
operations where the panels underwent
large deformations, slid, tilted, bent,
sagged
excessively or were subjected to any
other unusual conditions.
The building manufacturer should be
consulted to determine the warrantability
of their
product, given its current condition.
Also, they should be able to pass some
opinion on
the weather-tightness of their panels,
given their current condition.

Contact
Information
- Telephone:
- (517)
467-6145
- FAX:
- (517)
467-2220
-
- Postal
address:
-
- Structural
Solutions LLC
- 8466 Slee
Rd.
- Onsted, MI
49265
- Electronic
mail:
General Information:
Thomas R. Price,
P.E.

[ Home ] [ Engineering Services ] [ Gallery of Projects ] [ Request For Quote ] [ Resources ]
Copyright ©
2007 Structural Solutions LLC, 8466 Slee Rd.
Onsted, MI 49265 Lenawee County
|