(517) 467-6145 e-mail us
- Sample report of
crane bracing investigation
CRANE BRACING INVESTIGATION
I. Purpose of Investigation:
At the request of contractor, Thomas R.
Price P.E., of Structural Solutions LLC
inspected
the owner's facility for the purpose of
analyzing and making design
recommendations regarding
the crane system bracing, and a previous
building modification which raised one
crane runway
24", using column stubs.
II. Description of Building:
The building in question is a metal
building manufactured by an MBMA
manufacturer.
The building is a 180' wide by 220' long
x 28' eave gabled roof building. (ref.
Fig.
A). Two 60' wide overhead crane systems
run the length of the building.
III. History:
Manufacturer calculation package
indicates a 1993 design. At some point,
the north crane
bay runway beams were raised 24".
Excessive building movement has been
observed by occupants,
which in part, has led to this
investigation.
IV. Referenced Documents:
Manufacturer calculation package dated
1993. Job # 0000-00
Note: Manufacturer construction drawings
were not available.
V. Field Observations and Notes:
The inspection took place between 3:00 pm
and 4:30 pm. Our comments relative to the
inspection of the crane system are listed
below.
1) On at least one crane beam, cracks in
some of the cap channel to beam welds
were observed. This matter is being
treated seperately, and is outside the
scope of
this report.
2) Various crane and wind rod braces were
observed to be excessively loose, and
missing altogether. An earlier letter
from this office calls for replacing all
missing
braces, and re-setting all braces to
proper at rest tautness. The instructions
in this
letter, combined with the provisions of
this report, should remedy the
longitudinal
bracing and movement problems currently
experienced.
3) The stub columns used to raise the
north runway 24" lack longitudinal
bracing.
The details of the stubs were noted, and
recommendations are made below.
4) In reviewing the runway beams for
recommending a solution to the cracked
welds, It was revealed that the crane
bridges need to be spaced further apart
in order to avoid overloading the runway
beams. The Manufacturer calculations call
for a minimum 16'-0" spacing between
adjacent cranes, center to center of
wheels.
Spacers to this effect should be
installed immediately.
In addition, it appears that the beams
may be inadequate for the AISC design
check
on sidesway web buckling. Further
investigation into the runway beams,
bridge
spacing, and posted crane capacity is
strongly recommended.

Contact
Information
- Telephone:
- (517)
467-6145
- FAX:
- (517)
467-2220
-
- Postal
address:
-
- Structural
Solutions LLC
- 8466 Slee
Rd.
- Onsted, MI
49265
- Electronic
mail:
General Information:
Thomas R. Price,
P.E.

[ Home ] [ Engineering Services ] [ Gallery of Projects ] [ Request For Quote ] [ Resources ]
Copyright ©
2007 Structural Solutions LLC, 8466 Slee Rd.
Onsted, MI 49265 Lenawee County
|